Why even turn the AC on? If it is shorting he should be able to disconnect grounds one at a time until he no longer reads continuity/resistance/ohms between his hot wire and ground, right? Once the conductor that is shorted to ground is ID'ed its just a matter of finding out where it is shorted and resolve the problem.I think you have the hot and neutral wires connected properly because the lights worked fine when the grounds were not connected. Since grounding the system flips the breaker immediately (before turning on the lights), I think one of your hot pigtails is being grounded to the metal box it is in.
This is a dangerous situation. It means that one of your boxes is essentially wired to 120V. Electrocution hazard.
The safest course of action is to stop reading and call an electrician. If you are too stubborn to do that, then here is how I would debug if I was you
That is how I was debug if I was you. But I am not you. I would debug by unwrapping all the pigtails, tell my wife to leave the house, turn the breaker on, and then measure which box is at potential using a multimeter set to AC volts. But this places you in the presence of an electrocution hazard, and you admitted to being a dunce, so I like avoiding that.
- Turn off the breaker and leave it off until step 4
- Glance at each box and look for this type of fault. Hopefully you can spot it
- If that doesn't work, find the first box that you ran wires to from the breaker panel. Do these steps at that box only!
- separate the ground pigtail
- find the conduit the comes directly from the breaker box
- connect the bare ground wire from that conduit to the green screw on the metal box
- leave all other grounds floating in air, not touching each other
- Walk back to the breaker box and flip the breaker on
- If the breaker trips, then you know that the short is in that first box. Focus your effort there
- If the breaker doesn't trip after a few seconds, then turn it off and continue.
- Go back to the first box and connect one downstream ground wire to the ground wire that you connected to the green screw. You should have the ground from the breaker panel connected to the green screw and one downstream circuit. The other ground wires should still be floating in air and not connected.
- Repeat the breaker test. If it trips, then your shirt lies somewhere in the circuit that you just tied to the ground. If not, turn the breaker off and repeat.
- Keep fanning out away from that first box until you find the short.
- Only leave the breaker active for a few seconds at a time. Until you fix the problem, the breaker must be off before you walk away from the panel
good luck
H
Why even turn the AC on? If it is shorting he should be able to disconnect grounds one at a time until he no longer reads continuity/resistance/ohms between his hot wire and ground, right? Once the conductor that is shorted to ground is ID'ed its just a matter of finding out where it is shorted and resolve the problem
I think you have the hot and neutral wires connected properly because the lights worked fine when the grounds were not connected. Since grounding the system flips the breaker immediately (before turning on the lights), I think one of your hot pigtails is being grounded to the metal box it is in.
H