Diagnosing Whole Home Humidifer

AgronAlum

Well-Known Member
Jul 12, 2014
5,432
7,069
113
I’m fairly handy but don’t even know where to start. Our house was at 30% according to the thermostat on the main level, so I turned it up. We are now down to 27 and I have it set between 40 and 45. I don’t think it’s doing anything. Not sure it did much last year but had no way of knowing.

I know there’s water flowing from when I changed the filter. Outside of that, it makes no noise, there’s no readout and it’s a closed system.
 

herbicide

Well-Known Member
SuperFanatic
SuperFanatic T2
Mar 23, 2006
10,838
2,278
113
Ankeny, IA
It's probably simply not keeping up with the colder outside air which naturally drops the RH in a warmer house. Colder air has less water holding capacity, which means the same air heated up will have a lower RH than the colder air.
 

AgronAlum

Well-Known Member
Jul 12, 2014
5,432
7,069
113
It's probably simply not keeping up with the colder outside air which naturally drops the RH in a warmer house. Colder air has less water holding capacity, which means the same air heated up will have a lower RH than the colder air.

My thinking is the furnace is pushing air from the return which should already be at or near room temperature. The furnace is also running more than normal with colder temps, which means the humidifier should be running more. I guess if it can’t keep up in cold temps, I’m not sure what the point of it is.
 

kbud

Active Member
Jan 9, 2012
380
-49
28
Is the air damper open allowing warm air to pass across the media? Or does this unit have its own fan, is the fan operating?
 

AgronAlum

Well-Known Member
Jul 12, 2014
5,432
7,069
113
Is the air damper open allowing warm air to pass across the media? Or does this unit have its own fan, is the fan operating?

No damper. It’s hanging right on the return. I can barely see the humidifier itself because of the positioning. I’ll have to turn the furnace up to see if I can hear anything. This is the setup that was installed before we bought the house.

8BF97A97-27DA-4E4F-815E-BFA2D5648115.jpeg
 

Acylum

Well-Known Member
Nov 18, 2006
12,886
13,289
113
Those can play hell with your HVAC system. I would stop using it and just get a console unit.
 

herbicide

Well-Known Member
SuperFanatic
SuperFanatic T2
Mar 23, 2006
10,838
2,278
113
Ankeny, IA
That looks like a ductless model, which should have its own fan to draw air across the duct. Fan working?

Or is the duct on the other side where we can't see it in the picture?

Also, is it on the cold air side or the hot air side?
 

AgronAlum

Well-Known Member
Jul 12, 2014
5,432
7,069
113
That looks like a ductless model, which should have its own fan to draw air across the duct. Fan working?

Or is the duct on the other side where we can't see it in the picture?

Also, is it on the cold air side or the hot air side?

No ducts running anywhere. The only thing coming out of the unit is a drain line, the power supply and a water line. It’s on the cold air side.

I’ll have to check the fan. I can’t hear anything with the furnace on but it might just be the furnace drowning it out.
 

herbicide

Well-Known Member
SuperFanatic
SuperFanatic T2
Mar 23, 2006
10,838
2,278
113
Ankeny, IA
No ducts running anywhere. The only thing coming out of the unit is a drain line, the power supply and a water line. It’s on the cold air side.

I’ll have to check the fan. I can’t hear anything with the furnace on but it might just be the furnace drowning it out.

It "should" be on the hot side, as the hot air will hold much more water.

Also, a typo on my first post; the fan should draw the air across the pad.
 

h-man64

Active Member
Oct 18, 2006
105
44
28
West Des Moines
I always wondered if mine was working, so I bought a cheap humidistat which i placed on my mantal upstairs and adjusted the humidity accordingly.
 

CYdTracked

Well-Known Member
Mar 23, 2006
17,001
7,712
113
Grimes, IA
I have the same humidifier as you do and I haven't even turned mine on yet and still have about 40% humidity in my house. If you crank it all the way up do you hear it spraying mist when the furnace fires up? Do you get your HVAC inspected by someone before the winter? You could have a plugged line or bad sensor if it is not kicking in. I have a service plan with my HVAC so they check everything out before I even use it and the best way to tell if is working is to turn it way up and see if you hear it.
 

BigBake

Well-Known Member
Mar 17, 2006
6,762
618
113
48
U'dale
Is there a a blue switch on the opposite side of that housing to open and close the dampener to send air thru it. Mine has a dampener you have to open to get it to function in Winter.
 

TexCyted

Well-Known Member
Oct 30, 2018
219
300
63
42
DFW
I had the same issue awhile back. I checked the filter and it was corroded so bad the whole system failed. Check that.
 

AgronAlum

Well-Known Member
Jul 12, 2014
5,432
7,069
113
I have the same humidifier as you do and I haven't even turned mine on yet and still have about 40% humidity in my house. If you crank it all the way up do you hear it spraying mist when the furnace fires up? Do you get your HVAC inspected by someone before the winter? You could have a plugged line or bad sensor if it is not kicking in. I have a service plan with my HVAC so they check everything out before I even use it and the best way to tell if is working is to turn it way up and see if you hear it.

I did not have anyone go through the furnace this year. I just spent 4 grand replacing the AC in August so the coil and everything else was replaced. Furnace is going fine.

I’ll have to check it out more when I get home.
 

AgronAlum

Well-Known Member
Jul 12, 2014
5,432
7,069
113
Is there a a blue switch on the opposite side of that housing to open and close the dampener to send air thru it. Mine has a dampener you have to open to get it to function in Winter.

No ****? I’ll have to feel around for it. I cannot see the left side of the unit.